Dell™ PowerEdge™ T610 Technical Guidebook
19
AC POWER SUPPLY (PER POWER SUPPLY)
Wattage
870W (high output)
570W (Energy Smart)
Voltage
90-264 VAC, autoranging, 47-63Hz
Heat Dissipation
2968.6 BTU/hr maximum (high output)
1944.9 BTU/hr maximum (Energy Smart)
Maximum Inrush Current
Under typical line conditions and over the entire system ambient
operating range, the inrush current may reach 55A per power supply
for 10ms or less
C. Environmental Specifications
TEMPERATURE
Operating
10° to 35°C (50° to 95°F)
Note: For altitudes above 2950 feet, the maximum operating temperature is de-rated
1ºF/550 ft.
Storage
–40° to 65°C (–40° to 149°F)
RELATIVE HUMIDITY
Operating
20% to 80% (non-condensing) with a maximum humidity gradation of
10% per hour
Storage
5% to 95% (non-condensing) with a maximum humidity gradation of
10% per hour
MAXIMUM VIBRATION
Operating
0.26 Gms (10 to 350Hz) for 5 mins. in operational orientations
Storage
1.54 Gms (10 to 250Hz) for 10 mins. in all orientations
MAXIMUM SHOCK
Operating
Half sine shock in all operational orientations of 31G plus or minus 5%
with a pulse duration of 2.6ms plus minus 10%
Storage
Half sine shock on all six sides of 71G plus or minus 5% with a pulse duration
of 2ms plus minus 10%
ALTITUDE
Operating
–16 to 3048 m (–50 to 10,000 ft)
Note: For altitudes above 2950 feet, the maximum operating temperature is de-rated
1ºF/550 ft.
Storage
Storage: –16 to 10,600 m (–50 to 35,000 ft)